Like I already said to you in DM, if you wanna argue about the dangers of an incredibly common type of wiring please come back to me with new information that’s relevant, not just copy and paste from a google search on harmonics. Even the first sentence begins with…Sinusoidal currents on the phases of a 3-phase, 4- wire system…
We are talking about small LED lights in a house not a massive 3 phase installation. The differences should be obvious.
While you’re looking go refer to the Canadian Electrical Code for the actual rule pertaining to Neutral conductors and ballast lighting. See 2, a, i, ii
Be 4-018 Size of neutral conductor (see Appendix B)
- The neutral conductor shall have sufficient ampacity to carry the unbalanced load.
- The maximum unbalanced load shall be the maximum connected load between the neutral and
any one ungrounded conductor as determined by Section 8 but subject to the following:
a) there shall be no reduction in the size of the neutral for that portion of the load that consists
of
i) electric-discharge lighting; or
ii) non-linear loads supplied from a three-phase, 4-wire system;